hi been trying to use a dc ssr relay to switch 24 volt supply on and off for a unit i use that needs to see 0v or 24v but when the switch voltage is applied there is still 18v showing on the load side not zero ..does the ssr have to have a load on it to fully switch off and on from 0v to 24v ?
Mail from PST in UK
You are right you need a bleeder resistor of 10k or 100k to ensure the collector leakage current of SSR is bypassed to make you see a '0' when the SSR is off. If the SSR is working well, and no input or '0' control input then SSR output is high impedance and only a collector or diode leakage will hold the SSR output at the Full Voltage but it cannot drive any current. Hence a bleeder across output will show you a '0'. Use it if the bleeder does not cause any problems.
If you were driving a 5A Solenoid, then you would not see this problem. If you are driving a Solid State Load, such effects are natural. It is because the Solid State Load like a Electronic Circuit will draw current only on demand.
These instruction is for a Normally Open Output, NO. A Normally Closed NC is vice versa. And also some Special SSRs may have sensitive inputs, So a low impedance '0v' at input has to be ensured.
The Bleeder should bypass the leakage current, so one end of bleeder goes to SSR output and other end of bleeder goes to the ground or 0V point of your circuit which is controlled by SSR.